power factor
1. What Power Factor Is
Power factor ( or ) = ratio of real power to apparent power, also
where = phase angle between and ().
- : leads ⇒ inductive, lags (lagging pf, e.g., motor).
- : lags ⇒ capacitive, leads (leading pf, e.g., capacitor).
- : resistive or resonance, (unity) ⇒ all power real.
Range
(leading/lagging indicates sign of ). Lagging pf = inductive, leading pf = capacitive.
2. Why Power Factor Matters
- Real power (useful, W):
- Reactive power (stored, VAR):
- Apparent power (supplied, VA):
Utilities must supply ; low ⇒ larger for same ⇒ more losses in lines and larger equipment. So high (≈1) desired.
3. Correction
Inductive load ( lagging) can be corrected by adding capacitor in parallel (leading ) to bring toward 0, reducing .
4. Worked Examples
(a) Series RL: R=3Ω, X_L=4Ω ⇒ |Z|=5Ω, pf= R/|Z|=0.6 lagging (φ=53.1°) ⇒ P= V·I·0.6
(b) Load 1kW at 230V, pf=0.6 lagging ⇒ I=1000/(230·0.6)=7.25A vs pf=1 ⇒ 4.35A ⇒ 66% more current, more loss.
(c) Need to correct pf 0.6 to 0.9: add capacitor Qc = P(tanφ_old - tanφ_new)
(d) Pure resistor pf=1, pure L/C pf=0 (no real power).
5. Exam Points
- Define — 5 marks, very frequent (almost certain to ask definition).
- Show , , — 5-7 marks, very frequent.
- Distinguish lagging (inductive) vs leading (capacitive) — 5 marks, frequent.
- Need for power factor correction with capacitor — 5 marks, frequent.