Basic Electrical Machines (8hrs) · Basics of Electrical & Electronics Engineering

current ratio

Watch lectures

current ratio

1. What Current Ratio Is

Current ratio in ideal transformer is inverse of voltage/turns ratio:

I2/I1=N1/N2=V1/V2=aI_2/I_1 = N_1/N_2 = V_1/V_2 = a

(ideal, power in = power out: V1I1=V2I2V_1 I_1 = V_2 I_2 for unity pf, or complex V1I1∗=V2I2∗V_1 I_1* = V_2 I_2*).

So step-up voltage (N2>N1N_2>N_1) ⇒ step-down current (I2<I1I_2<I_1) and vice versa — conservation of power (minus losses).

For practical, I1=I0+(N2/N1)I2I_1 = I_0 + (N_2/N_1) I_2 where I0I_0 is magnetizing current (small, ~2–5% of I1I_1 at full load) due to core.

2. Relation to Turns

I1/I2=N2/N1=1/aI_1/I_2 = N_2/N_1 = 1/a

If a=V1/V2a= V_1/V_2, then I1=I2/aI_1 = I_2 /a. This is used for reflected current.

3. Worked Examples

(a) Ideal N1=100, N2=1000 (a=0.1 step-up 10× voltage), I2=10A ⇒ I1=100A ✓ Power: V1·I1 =230·100=23kW, V2=2300·10=23kW.

(b) Practical with I0=2A (magnetizing) and I2=10A, a=0.1 ⇒ I1= I0 + a·I2? Actually I1= I0 + (N2/N1)·I2? No I1= I0 + (N2/N1)·I2? Wait ideal I1_ideal= (N2/N1)·I2=10·10=100A, plus I0 vectorially (90° lag) ⇒ |I1|≈100.02A.

(c) Need to find primary current for 400V/230V step-down 1kVA load: I2=4.35A, I1= (230/400)·4.35≈2.5A.

(d) Why high voltage low current for transmission? P=VI constant ⇒ higher V lower I ⇒ lower I²R loss.

4. Exam Points

  • State I2/I1=N1/N2I_2/I_1=N_1/N_2 (inverse) — 3-5 marks, very frequent (often paired with voltage ratio).
  • Show power conservation V1I1≈V2I2V_1 I_1≈V_2 I_2 — 3 marks, frequent.
  • Mention practical I1=I0+(N2/N1)I2I_1 = I_0 + (N_2/N_1)I_2 — 5 marks, frequent.
  • Solve I1I_1 for given NN, I2I_2 — 3-5 marks, frequent.